The demand lighting load for a 10,000 ft2 motel with no dining room or ballroom is _____.

Prepare for the NCCER Load Calculations – Feeders and Services test with comprehensive practice material. Study using quizzes and detailed explanations to boost your exam confidence and ensure success!

Multiple Choice

The demand lighting load for a 10,000 ft2 motel with no dining room or ballroom is _____.

Explanation:
For interior lighting in lodging facilities, you determine the demand load by applying a fixed lighting load factor per square foot to the floor area. For a motel with no dining room or ballroom, the standard factor is about 1.02 VA per square foot. Multiply by the building size: 10,000 ft^2 × 1.02 VA/ft^2 = 10,200 VA. This reflects the expected usage pattern where not all lights are on at once, giving you the demand load rather than the total connected load. If dining rooms or ballrooms were present, the per-square-foot factor would be higher, leading to a larger demand load.

For interior lighting in lodging facilities, you determine the demand load by applying a fixed lighting load factor per square foot to the floor area. For a motel with no dining room or ballroom, the standard factor is about 1.02 VA per square foot. Multiply by the building size: 10,000 ft^2 × 1.02 VA/ft^2 = 10,200 VA. This reflects the expected usage pattern where not all lights are on at once, giving you the demand load rather than the total connected load. If dining rooms or ballrooms were present, the per-square-foot factor would be higher, leading to a larger demand load.