What is the ampacity for each of 8 No.2 THHN copper conductors in a single conduit?

Prepare for the NCCER Load Calculations – Feeders and Services test with comprehensive practice material. Study using quizzes and detailed explanations to boost your exam confidence and ensure success!

Multiple Choice

What is the ampacity for each of 8 No.2 THHN copper conductors in a single conduit?

Explanation:
Ampacity is the maximum current a conductor can carry without overheating its insulation in a given situation. When multiple current-carrying conductors share the same conduit, you must apply a derating factor because heat from neighboring conductors reduces the amount of current each one can safely carry. For No.2 copper THHN, the published ampacity at the 75°C rating is 115 A per conductor. With eight current-carrying conductors in the same conduit, the NEC derating table uses a factor of 0.70 for 7–9 conductors. Multiply 115 A by 0.70 to get 80.5 A. So the ampacity per conductor in this setup is 80.5 A. If you were using 90°C-rated terminations, you could apply a different base ampacity, but with typical terminations the 75°C-based calculation yields 80.5 A.

Ampacity is the maximum current a conductor can carry without overheating its insulation in a given situation. When multiple current-carrying conductors share the same conduit, you must apply a derating factor because heat from neighboring conductors reduces the amount of current each one can safely carry.

For No.2 copper THHN, the published ampacity at the 75°C rating is 115 A per conductor. With eight current-carrying conductors in the same conduit, the NEC derating table uses a factor of 0.70 for 7–9 conductors. Multiply 115 A by 0.70 to get 80.5 A.

So the ampacity per conductor in this setup is 80.5 A. If you were using 90°C-rated terminations, you could apply a different base ampacity, but with typical terminations the 75°C-based calculation yields 80.5 A.