What is the load in amps for a 3-phase 480V feeder supplying a load of 112.5 kVA?

Prepare for the NCCER Load Calculations – Feeders and Services test with comprehensive practice material. Study using quizzes and detailed explanations to boost your exam confidence and ensure success!

Multiple Choice

What is the load in amps for a 3-phase 480V feeder supplying a load of 112.5 kVA?

Explanation:
In a three-phase system, the apparent power S relates to line current I and line-to-line voltage V by S = √3 × V × I. So the current is I = S / (√3 × V). Here, S is 112.5 kVA (112,500 VA) and V is 480 V. Compute √3 × V = 1.732 × 480 ≈ 831.36. Then I = 112,500 / 831.36 ≈ 135.32 A. So the feeder current is about 135 A. If you check the other values, they'd require different S (e.g., 150 A would need ~124.7 kVA, 120 A would need ~99.9 kVA, 180 A would need ~149.9 kVA), confirming that 135.32 A is the correct match for 112.5 kVA at 480 V.

In a three-phase system, the apparent power S relates to line current I and line-to-line voltage V by S = √3 × V × I. So the current is I = S / (√3 × V).

Here, S is 112.5 kVA (112,500 VA) and V is 480 V. Compute √3 × V = 1.732 × 480 ≈ 831.36. Then I = 112,500 / 831.36 ≈ 135.32 A.

So the feeder current is about 135 A. If you check the other values, they'd require different S (e.g., 150 A would need ~124.7 kVA, 120 A would need ~99.9 kVA, 180 A would need ~149.9 kVA), confirming that 135.32 A is the correct match for 112.5 kVA at 480 V.