What is the minimum general lighting load in VA for a 12,000-square-foot office building?

Prepare for the NCCER Load Calculations – Feeders and Services test with comprehensive practice material. Study using quizzes and detailed explanations to boost your exam confidence and ensure success!

Multiple Choice

What is the minimum general lighting load in VA for a 12,000-square-foot office building?

Explanation:
In sizing feeders and services, you estimate the general lighting load by using a baseline wattage per square foot for the occupancy and multiply by the area. For a office space, the minimum general lighting load used in these calculations is 1.3 VA per square foot. So for 12,000 square feet, the minimum load is 12,000 × 1.3 = 15,600 VA. This is the baseline minimum; actual installations could be higher with more lighting or fixtures. If you used different per-square-foot values, you’d get other totals (12,000 VA at 1.0 VA/ft², 18,000 VA at 1.5 VA/ft², 19,800 VA at 1.65 VA/ft²).

In sizing feeders and services, you estimate the general lighting load by using a baseline wattage per square foot for the occupancy and multiply by the area. For a office space, the minimum general lighting load used in these calculations is 1.3 VA per square foot. So for 12,000 square feet, the minimum load is 12,000 × 1.3 = 15,600 VA. This is the baseline minimum; actual installations could be higher with more lighting or fixtures. If you used different per-square-foot values, you’d get other totals (12,000 VA at 1.0 VA/ft², 18,000 VA at 1.5 VA/ft², 19,800 VA at 1.65 VA/ft²).